To clarify- what I have is: 1. Manual stencil print process 2. Dynapace conveyor into GSM 3. Dynapace conveyor out of GSM into oven So what I need is a way to tell the conveyor into the placement machine to "go" when a board is loaded onto it after
Electronics Forum | Tue Nov 10 00:18:52 EST 2015 | ttheis
How is a board conveyor typically configured to unload into a conveyor oven if there is no downline machine to five a ready to receive signal? Do you just use a plc to activate the machine ready signal at a timed interval? Would you perhaps do the sa
Electronics Forum | Wed Dec 30 11:10:53 EST 2015 | ilavu
Tom, Mount one sensor at about 6 inch inside of the beginning of the oven conveyor and use its output as ready to accept the board signal. That 6 inch distance will give you timing and space between two boards entering in the oven. Tushar
Electronics Forum | Tue Nov 10 10:31:57 EST 2015 | jimmyboz
What is your goal? To keep feeding boards regardless,or to stop feeding boards if they are not coming out?
Electronics Forum | Wed Dec 30 11:24:51 EST 2015 | ttheis
Hi Tushar, That is the conclusion that I was coming to before Gary's suggestion. I think a sensor will probably be the best solution but it is good to have options and back-up plans. Thanks everyone
Electronics Forum | Sun Nov 15 18:52:15 EST 2015 | ttheis
I presume start by having it just pass into oven as soon as it is given a board from the placement machine. If I find I need to pace the boards into the oven it seems a basic PLC would be needed? Thanks for the help.
Electronics Forum | Tue Dec 29 13:59:43 EST 2015 | ttheis
Hi Gary, Thanks for the tip, I'll give that a shot!
Electronics Forum | Tue Dec 29 11:38:40 EST 2015 | g2garyg2
Hi Tom If the DYNAPACE has SMEMA out all you need to do is place a two wire jumper into pins 3&4 or 1&2 depending upon DYNAPACE's SMEMA configuration. This will by-pass a Release signal and feed PCBs into the oven.
Electronics Forum | Thu Sep 29 20:08:17 EDT 2022 | proy
I have an 8130 Magazine loader (end of line boards into magazines) Has anyone here converted one of these to SUPPLY boards FROM the magazine to the printer/conveyor?
Electronics Forum | Thu Oct 18 15:03:48 EDT 2012 | rway
2) Start with the PLC. What do the indicator lights tell you. Is your entry sensor working? Your PLC has status lights that should go on/off with the input/output conveyors. Can you be more specific about "not operational?" This is a broad stat